[ale] Enclosed Desks
Jeff Hubbs
hbbs at attbi.com
Sat Jun 22 12:30:03 EDT 2002
On Sat, 2002-06-22 at 12:17, Christopher Fowler wrote:
> Consensus states to take off the door. No problem. I prefer to take it
> off then leave it open anyway.
>
Chris, even at that you might want to be careful about that
hot-air-ingestion issue.
I think all IT people should have a good thermometer; I use mine pretty
often (thermocouple module + Fluke DVM in my case). I'd measure the
intake/exhaust air temps with the computer standing on a table in the
middle of a room for reference purposes and then measure again with the
box in the cabinet (load it up with a kernel compile or something - hey,
I know, I'll give you my SETI at Home ID :-) ). If the exhaust temp is
higher even though room air temp is the same, then you are probably
having a reingestion problem.
- Jeff
---
This message has been sent through the ALE general discussion list.
See http://www.ale.org/mailing-lists.shtml for more info. Problems should be
sent to listmaster at ale dot org.
More information about the Ale
mailing list